  :: Design practice for the earthing system
  :: °ü¸®ÀÚ 2007-06-13 17:12:06 , Á¶È¸ :1172906  
  :: File download   [pdf : 2144 KB  Download: 10020]
Design Practice for the Earthing System
of the 400 kV Gas Insulated Switching Station at Lavrion
 
G. J. Georgantzis
Public Power Corporation of Greece
Athens, Greece
N. G. Gagaoudakis
Public Power Corporatioll of Greece
Athens. Greece
TIL Connor
Siemens AG
Erlangen, Gennany
 
Abstrad: The paper presents the situation of the gas insulated 400 kV switching station at Lavion (If Public Power Corporation, Greece as a part of a power station expansion project and gives details of the" groued grid design.
  Although the grotmd grid design was carried out according to the American Standard IEEE 80 "Guide for safety in AC substation grounding", there is a cross reference to the Gcnnaa Standard DIN VDE 0141 "Earthing systems for power installations with rated voltages above t kV" and the upcoming European Standard EN 50179 "Ereetion of electrical power installations in systems with nominal voltages above I kV AC"
  Besides the analysis of soil res.istivity wd the selection of con- ductor Sizes, the detennination of fault current distribution in Lie grounding system is a key step for the design of an effective and economically feasible grounding system.
  Finally, the test procedure for verification of effectiveness of the earthing system a6er completion of erection is given.

Keywords: Grounding SYSI.em design, GIlS insu!at.od swilchgear, Electromagnetic compatibility
 
l.introductton
  A closed type, metal enclosed, SF6 gas insulated 400 kV switching station, h.as been constructed and put in operation in 1998 at the area of Lavrion, to serve the new Lavrion 550 MW combined cycle power plant with three gas and one steam rurbine units, as well as the existing 300 MW old steam rurbine unit. One, already existing, double circuit overhead line together with a new one single circuit under construction transmit the power into metropolitan Athens area. The s witching station with double busbar and nine 400 kV bays in total is the first in that voltage level in Greece. A simplified layout of the switching station is presented in Fig. 1.
   Apart from the above units, there are also in operation at site one ISO MWoil frred steam rurbine and one combined cycle unit with total rating of 175 MW feeding power at 150 kV voltage level through an air insulated 150 kV substation.
  The limited dimensions of the available space, almost 9000 m", as well as the great industrial and sea pollution
problems at site, made the decision of constructing a compact closed type gas insulated switchgear (GrS) substation obligatory.
   GIS substalions offer a lot of advantages to utilities. They need only small areas compared to outdoor conventional type switchgear. they are independent from environmental conditions and can be considered very reliable. Therefore, they are found in load and generation centres, where the leve l¡¤ of short circuit capacity is high.
  These facts have an impact on the ground grid design. which has to guarantee a safe substation with regard to step and touch voltages. Also the interference with other systems nearby, like control systems, has to be minimised in order to maintain operation under fault conditions and to secure the quality of power.
   All the above mentioned units and the related switchgear are close together fonning a llDified power complex of
1200 MW occupying an area of about 400 000 ml. Consequently tbe earthing network of the new closed type GIS
substation could be assumed as-a part of the larger earthing nmvork of the whole complex. Nevertheless for safety reasons, it is faced as zn independent selfstanding network suitable to assure 310ne safe operation and the protection of the staff in C3se of earth faults.
   In this p3per description and details of the grounding grid design both outdoor and indoor. together with the foreseeable electromagnetic compatibility measures, are given. Although the design was carried out according to the American Standard IEEE 80 "Guide for safety in AC substation grounding" [1, 2], there is a cross reference to the Gennan Stand.lJd DIN VDE OJ41 "Earthmg systems for power installation with rated voltages above I kV" [3] and the upcoming European Standard EV 50179 "Erection of electrical power installations in systems with nominal voltages above I kV AC" [4].
  The paper especially discusses the detennination ofsoil.resistivity, the selection of material and cross section of ground conductors. the tolerable touch and step voltages, the expected .ground potential rise, the design details and the rest procedure for verification of effectiveness of the earthing system after completion of the erection.
 
II. Determination of Soil Resistivity
  In order to design the earthing system afthe substation. the resistance to earth has to be calculated in advance. This value depends on two parameters whictl can hardly be influenced by the designer. The area covered by the installation and the specific soil resistivity beneath, As the specific soil resistivity varies considerably with type and structure of soil the reliable detennination of effective soil resistivity is essential for a safe aJld ec()Tlomic design,
  In order to detennine me soil sIDlcrure also in deeper layers, the Wenner method, which uses 4 electrodes at the surface to measure soil resistivity also in larger depth; has proved to be a useful tool. The resulting diagram of apparent soil resistivity is the basis to identify top and bottom layer resistivity as well as top layer thlclcness.
  For the Lavrion site out of 4 sequences with spacing up to 30 m the decisive parameters were taken,
  Pr = 160 §Ù ¡¤m top layer resistivity
  PB = 60 §Ù ¡¤m bottom Jayer resistivity
  h = 13 m top layer thickness
Considering, the area of the intercoonecled earth grid of substation and power station of more than 160000 §³ , the
effective equivalent resistivity for a homogenous soil comes to 68 §Ù ¡¤m
 
Ill. Thermal Design
  The task of earthing conductors is to carry the line to ground fault current from the fau lted component and distrib¡¤
ute it to the buried earth electrodes. Tne siring has to be done in 3. way that no damage or melting will occur even in case of auto reclosure or subsequent faults in short sequence.
The design for the 400 kV equipment was based on the following parameters:

  
   For copper conductors this results in a required minimum cross section of 220 rnm2? For earthing conduc tors of equipment which is connected at least twice or for the meshed part of the grid a split up of current can be considered. In this case a copper cross section of 150 mm1 is sufficient.
 
IV. Tolerable Touch and Step Voltages
  In case of a line to ground fault a person in or outside the substation can be subjected to a potential dirference between hand and feet, hand and hand or foot and foot. This potential difference will lead to a cumnt through the body, which. has to be limited to a safe level not causing ventricular fibrillation of the hew. Based on the current limit found by Dalziel, the IEEE standard 80 gives fonnu las to detennine tolerable touch and step voltages under consideration of body and feet resistances as well as fault duration:
 
V. Determination of Expected Ground Potential Rise
  In case of a line to ground fault in the substation area the fault current will return on different path. Part of the fault
current will flow through me interconnecred earth grid to the grounded neutrals of the generator transfonners. Another part will return due to inductive coupling through the ground wires of the outgoing overhead lines. The rest will be split up according to the ratio of resistances between substation earth grid and power station earth grid.
The resistance to earth of an earth grid lies in between the value of a solid plate and a single earth electrode surroWlding the area. The fonnu la according to IEEE 80 considers the actual dens ity of the meshed grid by taking into account the length of the buried conductors.
 
VI. Check of Design regarding Touch and Step VOltages
  Based on the expected ground potentlaI rise it was decided to install in the substation area not covered by fo undations a buried earth grid wilh rectangular meshes having a maximum mesh width of 10 m. The calculation of mesh voltage according to the formulas of IEEE SO gave Umeln co 422 V. As this mesh voltage is smaller than the tolerable touch voltage, the design requirements with respect to touch voltages are fulfi lled. The analysis of step voltages gave Ustep = 278 V, which also satisfies the requirements of tolerable step vo.1tages.
 
VIl. Details of Earthing System Design
  The main oomponents of the earthing system are the meshed and buried outdoor earthing grid, the foundation
ground electrode of the buildings and the indoor earthing system. The structure is given in Fig 3.
  In order to fonn a foundation ground electrode steel bars are welded together and embedded in the concrete of the
lowest floor. The steel bars are wrapped to the reinforcement rnats and have risers to the indoor earthing system.
   A main earthing conductor which runs along the wall is the backbone of the indoor earthing system. All components which can carry the fault current are connected via earthing conductors to the main earthing conductor at least twice.
There are several connections to the outdoor earthing system,
  High voltage gas insulated switchgear causes transient potential differences when isolators are switched. In order to prevent arcing between grounded metal strucrures and to reduce interference on secondary equipment, additional measures with respect to electromagnetic compatibility are considered,
  Equipotential bonding for high frequencies
  Enclosure earthing in a low inductive manner
  Secondary wiring ~ith suitable screens
  Rooms of the control building with sensitive equipment are shielded in order to minimise interference from electramagnetic fields radiated from 400 kV outdoor bushings during isolator switching.
  There are earth wires between the metal support of the surge arrestors and the 400 kV bushings of the outgoing
overhead lines,
  Each building is surrounded by a¡¤ potential control electrode in 1 m distance to the building. The lightning protection system is interconnected with the earthing system.
 
VIII. Current Injection Test
  In order to check the effectiveness of the earthing system it is intended to carry out a current injection test after completion of the erection. For this purpose an outgoing overhead line will be short circuited and grounded in about 6 km distance.
In the substation a single phase current source will be connected between¡¤ the tbiee phase conductors of the overhead line and the substation earth grid (Fig. 4). The test current will be about ISO A. During the test the following data are recorded
  Ground potential rise
  Touch voltages and transferred potential
  Step voltages
  Potential differences within the earth grid
  Zero sequence impedance of test line
 
IX. Design Procedure according to German Standard
  The DIN VDE standard 0141 requires a design of the earthing system with respect to thermal and mechanical
stresses., as well as a design to meet touch voltage requirements. While the thermal design gives almost the same results as IEEE 80, the approach to meet touch voltage requirements is different.
  It is presumed that the calculation of ground potential rise is far more accurate and easy to handle than the theoretical determination of touch voltages.
  The tolerable touch voltage can be taken from a diagram giving the tolerable touch voltage as a function offau!t duration. This diagram is based on the body current limits given in lEe 479 [5]. In VDE it is stated that the correct operation of protection and circuit breakers can be presupposed. As the tolerable touch voltage according to VDE is not considering feet resistances, the value is smaller than the IEEE value.
   There is no step voltage limit given in VDE 0141.
  
 
x. Earthing requirements of upcoming European Standard
  With the upcoming European Standard EN 50179 the requirements for earth grid design of a substation will be part
of a general standard for the erection of high voltage installations.
  The thennal design will be similar to the procedure known from IEEE and VDE.
  The design with respect to touch voltages is based on the VDE approach. There is a diagram giving the tolerable touch voltages in dependence of fault duration. Additional curves give limits for touch voltages under consideration. of foot and shoe resistances. As there is no formula to calculate touch voltages there are certain circumstances listed under which the earth grid can be considered as sufficient to keep touch voltage limits.
  
  
 
XI. Sununary
  The careful design of an earthing system for a substation is necessary to assure not only the protection of the staff, but also the safe operation, in case of eanh faults. Substations with gas insulated Switchgear need even more efforts because ofthetr limited dimensions.
   The closed type, metal enclosed, SF 6 gas insulated 400 kV switching station at Lamon, the first in that voltage level in Greece, has been constructed and put¡¤into operation in -1998 .
  As some of the main components of the earthing system are integrated into the civil works, it was essential to design me earthing system at the very beg;irming of the project.
   Details of the design, which was carried out according to the American Standard IEEE 80, arc given in the paper. As a cross reference the requirements of the German Standard DIN VDE 0141 and the upcom ing European Standard EN 50179 are given. The aspect of electromagnetic compatibility in the surrounding of the GIS was considered.
  Finally Ihe test procedure for verification of the effective-ness of earthing system after compl etion of erection is given.
 
XII. References
[1] ANSUlEEE Std 80-1986 "Guide for Saf~ in AC Substation Grounding"
(2] ANS1JIEEE Std 81-1983 "Guide for Measuring Earth Resistivity, Ground Impedance and Earth Surface
Potentials of a Ground System"
[3] DIN VDE 014 1-1989 "Erdungen fur Starksttomanlagen mit Nennspannungen Ober 1 kV"
[4] prEN 50179-1996 "Erection of electrical power instaUations in systems with nominal voltages above I kV AC"
[5] LEe 479-1/1 984 "Effects of current passing through the human oody"
 
XIII. Biographies
  :: File download   [pdf : 2144 KB  Download: 10020]
Àüü¸ñ·Ï  ¼öÁ¤  »èÁ¦  Àμâ 
139
¹øÈ£ Á¦    ¸ñ ÀÛ¼ºÀÚ ÆÄÀÏ µî·ÏÀÏ Á¶È¸
109 ZnO Varistors 1467 KB °ü¸®ÀÚ 2007.06.13 116351
108 Dynamic impulse conduction in ZnO arresters 1737 KB °ü¸®ÀÚ 2007.06.13 123055
107 Design practice for the earthing system 2144 KB °ü¸®ÀÚ 2007.06.13 1172906
106 Experimental study on lightning breakdown channels in the... 1245 KB °ü¸®ÀÚ 2007.06.13 119521
105 ³«·Ú¹æÀü ±×¸²ÆÄÀÏ 1359 KB °ü¸®ÀÚ 2007.06.13 12096
104 Protection From Incoming Power Line Voltage Anomalies 250 KB °ü¸®ÀÚ 2007.06.13 14022
103 lightning imaging sensor - NASA 563 KB °ü¸®ÀÚ 2007.06.13 10471
102 TVSS 719 KB °ü¸®ÀÚ 2007.06.13 11815
101 MOV 208 KB °ü¸®ÀÚ 2007.06.13 18725
100 Protection of MV/LV substation transformers 162 KB °ü¸®ÀÚ 2007.06.13 18464
99 intelligent LV switchboards 148 KB °ü¸®ÀÚ 2007.06.13 26276
98 Dynamic stability of industrial electrical networks 101 KB °ü¸®ÀÚ 2007.06.13 12324
97 electrical installation dependability studies 120 KB °ü¸®ÀÚ 2007.06.13 13722
96 active harmonic conditioners and unity power factor recti... 163 KB °ü¸®ÀÚ 2007.06.13 10871
95 LV circuit-breakers confronted with harmonic, transient a... 90 KB °ü¸®ÀÚ 2007.06.13 14792
[1] [2] 3 [4] [5] [6] [7] [8] [9] [10] | [Prev] | [Next] |
Copyright © 1998-2015 by Ground.Co., Ltd., All rights reserved.
ÆäÀÌÁö »ó´Ü
ÇѱÛViewer ´Ù¿î·ÎµåAcrobat Reader ´Ù¿î·Îµå